Dear Experts:

I am using a Eurotherm 2216e Temperature Regulator in conjunction with LabView 7 over an RS232 interface.

NI.com has drivers for this device, which I downloaded. I was able to finally get the Process Value Monitoring Example.vi to work by adjusting the baud rate.

I am now trying to use the Temperature Control and Monitoring Example.vi and I am having problems.

During startup the vi (Temperature Control and Monitoring Example.vi) is able to get through the first two major blocks:
1 – ET24XX Initialize.vi
2 – ET24XX Set Instrument Mode.vi

Once I get to the vi gets to the ET24XX Instrument Configuration.vi block I get an error ERR (-1074001423).

Has anyone had this problem?

Thanks

Owen
0 Kudos
Message 1 of 8
(7,101 Views)
I communicate with Eurotherm instruments using Labview. I have not used the drivers that you are using. I am using a Modbus VI to get process values and change the setpoint. What are you trying to do? I also use the iTools OPC server with Labview. This is the best way to go, if you don't mind buying the software.
0 Kudos
Message 2 of 8
(7,096 Views)
One of the vi's included in the package from NI allows you to regulate and monitor the temperature. That is really all that I want to do.


I want to be able to heat up a surface for temperature dependant tests and monitor this temperature. Nothing fancy.

Any further help is really appreciated.

Thank you.

Owen

PS: The drivers that I am using are at the following link, the ones for the 24XX series that should also, in most part, work for the 22XX series.

http://sine.ni.com/apps/we/niid_web_display.drv_results?p_app_area=&p_man=eurotherm&p_keywords=&p_inst_type=&p_env=&p_drv_type=&p_int=
0 Kudos
Message 3 of 8
(7,093 Views)
Here are two VIs that I use. I think that if you want to use com1, you really select com2, but I forget. You need to make sure your instrument is set up for modbus comms and address1.
0 Kudos
Message 4 of 8
(7,079 Views)
Looking at the particular VI that you reference (ET24XX Instrument Configuration.vi) and comparing addresses in it with valid Modbus addresses for the 2216e, it is very likely that the problem lies with the addresses that are always written to in that particular VI that are not actually appropriate for the 2216e. If you do not already have a copy, I suggest that you obtain a PDF copy of the 2000 series communications manual from a eurotherm website and compare all the addresses that are used in this VI with those that are valid for a 2200 - these addresses can all be found in section 5 of this manual.

Best Regards,

Russell Read. Eurotherm Technical Support - US
0 Kudos
Message 5 of 8
(7,072 Views)

Hi, 

 

I insert myself on your discussion because I am using too an eurotherm 2216e, but in EI Bisynchrone and not in Modbus; I don't find any VI on NI site;

 

Do you know where I can find it? 

 

Thanks

 

eurolab 

 

 

 

0 Kudos
Message 6 of 8
(6,165 Views)
Take a look at this post.  There is an example in there.  http://forums.ni.com/ni/board/message?board.id=170&message.id=191952&query.id=570855#M191952
0 Kudos
Message 7 of 8
(6,146 Views)

Hello

 

Always with my 2216e on EI-Bisynchrone whith labview, I have now a problem for the execution: i am sending mnemonics "pc", and "2", which normally would put the program at the state of execution, but there is just the message "End" on the eurotherm;

 

Sending other orders, like temperature of ramp, is working.

 

Is anyone already had this type of problem?... Or see what can be the problem?

 

thanks

0 Kudos
Message 8 of 8