EthenetIP Tag Read / CIP Error Extented status may be available / CIP error 0x4
i am using Labview 2018 SP1 with Ethenet IP adapter toolkit 18.0.
I am connected to an Ethernet IP device (Zumbach ODAC laserHead) at the adress 192.168.1.30.
but i did not succeed in reading any Tags. i always have the error 0x4 .
i assumed the spelling of the tag ( prefix.suffix) is not right
so I connected a Scheiner PLC to the device to load the .eds file and read the Tag, it works perfectly well.
I copied the tag name in the labview code ( Inputs.Measure_Dimension_1) , it is not working.
I attache the screen shot of the PLC interface and the labview code with the error.
if someone have any idea of what i should do or try ...
(4,037 Views)
This thread help me solve a similar problem attempting to communicate to an Allen Bradley Micro820.  In the Micro820 I observer the following behaviors:
If I attempt to append the backplane slot and port to the network path I get error code and message:
-251723760
EthernetIP Tag Read DINT.vi;
Details: CIP Error - Extended status may be available
CIP Status: 0x1 (Connection failure)
CIP Extended Status: 0x311 (Port not available)
 If I accidently enter in the HMI IP address instead of the Controller I get:
-251723760
CIP Status: 0x8 (Service code unsupported)
However, if I eliminate the backplane slot and port and interface the HMI I get a different error message:
-251723760
CIP Status: 0x4 (Invalid segment type/IOI)
In summary, using only the IP address as the network path, allowed me to read the Micro820 data without errors!
Thanks for the clue that helped me resolve my issue!!!
(3,671 Views)
i don't get it ; you still have the issue ' 0x4' . right ?
here i also always get the error, i never found out a solution to read the tags in the device , when it is so easy with a plc.
Emmanuel
(3,640 Views)
Thankfully for me, I was able to read the Micro850 Tags without errors!
My first mistake was accidently attempting to communication to the HMI instead of the PLC.  When communicating to the PLC, I was still getting an error, because I had appended the backplane slot and port number as part of the Network address (192.168.0.140,1,0).  When I removed the backplane and port number (192.168.0.140) I was able to read the PLC Tags, without errors!
It seems like each controller behaves a little bit differently.  Did you try adding a backplane slot and port number to the Network path?
Good luck!
(3,625 Views)
