03-11-2020 10:09 AM
Hello All.
Very new here, Just started learning lab view.
Going through the core courses and making projects.
I am stuck with a thermocouple project...
Everything is starting to take shape, but I still cannot get the scaling right so the temperature is displayed in degrees C...
This set up seems to have come up a few times in core 1, but the scaling just seems to work...
maybe sombody here could take a look at my Vi and suggest where i might be going wrong.
Help appreciated! Thanks in Advance!
Toby
Solved! Go to Solution.
03-11-2020 10:33 AM
A few possible points:
I'd strongly suggest using instead DAQmx - see Learn 10 Functions in NI-DAQmx and Handle 80 Percent of Your Data Acquisition Applications for some starting guidance.
Beyond that, the scaling "should" work (probably, again, I'm not sure the behaviour with the blue wires 😮 ) so
03-12-2020 03:06 AM
Thanks for your reply!
yes, the 6kHz setting was me just experimenting and i had not changed it back to a more appropriate level.
I have some filtering on because there is a lot of noise where I am.
I have tried playing with the DAQ mx way of doing things too, this is used a lot on the core course.
i have attached a vi. that is basically taken from teh core course but set up to read from my thermocouple. I get the same issue there, it does not scale the readings to degrees C.....
the CJC is roughly right, the feed I am getting on my indicators is in the range of -2000000... so i dont think this is a CJC problem.
yes, the thermocouple is the correct type
i dont have any calibration information.
I have the thermocouple running through an instrumentation amp and then to NI USB-6000
The response i am seeing on MAX is correct visually. Also correct on the vi. the temp reading goes up as i would expect when the thermocouple is put in warm water.
It is just the scaling...
as far as I can tell, you are right! the scaling should just "work" but it does not...
03-12-2020 08:57 AM
You have a large negative temperature. Do you have the thermocouple wires swapped?
In the US for type K yellow is plus and red is minus. Here is the full colour listing:
https://www.madisonco.com/thermocouple-reference
03-12-2020 09:29 AM
@TobyETO wrote:
the feed I am getting on my indicators is in the range of -2000000...
..
Sounds like an open thermocouple. Disconnect the TC and see if it changes....
03-12-2020 10:30 AM
@EamonnFPMcKernan wrote:
You have a large negative temperature. Do you have the thermocouple wires swapped?
In the US for type K yellow is plus and red is minus. Here is the full colour listing:
https://www.madisonco.com/thermocouple-reference
But OP says the direction is as expected...
Do you couple the wires anywhere else (i.e. between the 'sensor' and the DAQ device/CJC)?
If you're changing the wire material (basically unavoidable if you're connecting to a non-TC specific extension cable) then that can cause offsets. Not sure if it can cause such a large offset...
03-12-2020 11:02 AM
I don't know what an OP is, but swapping the wires should be an easy test. Did you try this? Since you say the system responds to temperature changes I doubt it's disconnected, though maybe just one wire could be disconnected. Here is a table of voltage vs temperature if you have a multimeter handy.
https://www.thermocoupleinfo.com/type-k-thermocouple.htm
I use thermocouple wire for extensions, such as sold by Omega. Can you just hook up the thermocouple to your system for testing without the extension wire of the wrong material?
03-12-2020 11:06 AM - edited 03-12-2020 11:07 AM
@EamonnFPMcKernan wrote:
I don't know what an OP is
Sorry - "original poster", or sometimes original post. I guess also a great many other things, but I'd guess those are the most likely in a forum.
03-13-2020 05:21 AM
So,
The TC is definitely fully connected.
I tried reversing the wires but this did not bring the figure down.
below is a screen shot of test panels in MAX, here the amplitudes seem quite fine...
So why when it goes through the vi does it go totally crazy?
03-13-2020 05:28 AM