crio bricked 9066

Solved!
Go to solution
Im over in Germany
and a cRIO-9066 controller we have is unresponsive.



I arrived at it and it was running labview 14 with some previously installed
software. I needed to update the software so as my laptop has version 15 it
asked me to update the firmware. So I clicked update and it sent me to a

location on my C: drive called:



C:\Program Files (x86)\National
Instruments\Shared\Firmware\cRIO\7743\cRIO-9066_3.0.0f0.cfg



I put this on now the machine flashes the yellow statuss light continuously and
wont respond



Please could someone send me the usb flash drive files to recover it? I tried a
usb cable but to
0 Kudos
Message 1 of 4
(4,685 Views)
Solution
Accepted by topic author Monkins

The cRio was indeed bricked and safemode needed to be restored. 

Instructions and files for recovery have been comunicated via technical suport.

Regards,
Guy

Message 2 of 4
(4,598 Views)

Hi Everyone!

 

I also have a cRIO 9066 with firmware version 3.00.

In LabVIEW/MAX (18.0.0) I tried to configure the hardware. It is in safe mode, the yellow led blinks 2 times.

I can see it and configure the system and network related issues but at the software tab I see a message that firmware should be updated to at least 5.0.0.

I have found version 6.0.0. in patch NIRIO15.01, ut when I try to update it (from the file cRIO-9066_6.0.0.cfg), an error message comes:

 

"There was a problem updating the firmware for this device.
Error code: 800407E2"

 

I have no idea what can be the next step or what I have made wrong.

 

Thanks in advance for your help,

Attila

0 Kudos
Message 3 of 4
(3,079 Views)

That would have been cool if the instructions for unbricking were *Here* instead of someone's mailbox.

Message 4 of 4