I connected a pressure measurer to my Tc- 2095, the measurer as got an output of 1 V when the pressure is eagle to 0 but in NIMAX indicate 0.6 V why?
Is the tc-2095 fitted to measure a tension from 1 to 5V ? Why 1V became 0.6V? The channel was correctly setted to Volts , are there other set-up to do?
Thanks
Matteo
10-09-2013 09:39 AM
10-10-2013 03:00 AM
Ah ok .... than , do you think that's a calibration problem?
10-10-2013 09:21 AM
10-10-2013 09:36 AM
the tc- 2095 is connected to an SCXI 1102 and the measurer is a DRUCK pressure transmitter , model PTX 1000 (range 0-300 mBar)
10-10-2013 11:31 AM - edited 10-10-2013 11:38 AM
The 1102 is designed for thermocouple measurements. How are you connecting the pressure transmitter?
Edit-a quick check shows the ptx-1000 is 4-20ma.
10-14-2013 04:19 AM
Yes but i'm acquiring in voltage thant the 1100 as got a range of +- 10V and my instrument as got a range from 1 to 5 V
10-14-2013 04:28 AM
sorry 1102 ... the specifics are the same
10-14-2013 10:54 AM
10-14-2013 11:03 AM
I have my pressure measurer linked to my tc-2095 and the 2095 is connected to my 1102. I transform the current in voltage with a resistance of 249 omh.