About 40 second delay in Modbus communication

Solved!
Go to solution

Hello there!

I have a small problem using the following modbus library for LabView8.6:

Modbus Library

 

After I have started the Slave Demon it takes about 30 - 50 seconds for the first values (send via TCP/IP) to arrive. I have a Graph that plots all the18 read values for me and it always takes a long time to see them jump fom 0 to another value. Afterwards there remains a delay of about 30 seconds regarding how current the shown values are.

I can't post the VI here because it uses a lot of SubVIs which would make it not runable anyway. However, I already checked the Modbus Salve Example VI and there I have the same delay as in my own programm.

Anyone got any ideas?

 

 

Thanks in advance and kind regards,

Kamil

0 Kudos
Message 1 of 2
(4,022 Views)
Solution
Accepted by topic author Kambra

Problem solved. It was the device (a data logger) that was acting so slow in sending the data while it was acting as the master. I changed it now to be the slave and read its holding registers. This way the values arrive "immediatelly".

0 Kudos
Message 2 of 2
(3,998 Views)