03-04-2014 06:09 PM
Hello,
I have a cRIO 9024 with a Comsoft PROFIBUS module in slot 1. Following instructions provided, I am able to download the configuration.
However, the LED on the module are as follows:
PWR: Green
SPI: flashing green
RUN: Green
BF: Red
Looking at the manual, it tells me the possible reasons are a a configuration error or a non-responding DP-Slave.
I have attached a screenshot of my configuration, but I don't think I've made any mistakes, and the pumps are all configured to the bus addresses (3-14). I've checked the cables and they are all connected (daisy-chained.)
What could be the source of this error?
-Larry
03-04-2014 07:44 PM
try going online and see what happens.
03-05-2014 10:48 AM
Hello Jesse,
Do you mean the Monitor/Modify connect button the the Configurator? When I press it, all the slaves show up as red, and when I click on the property of one of them all the inputs/outputs show up as "fault."
03-05-2014 11:47 AM
Hi Larry,
That is the correct button. The configurator isn't finding your slaves, I would check that they are online and configured correctly. Once they are configured correctly they will show up as green in the configurator.
03-05-2014 11:59 AM
Jesse,
The PROFIBUS is connected to 7 Grundfos SMART Digital DDA metering pumps. They should be connected, have power, and I have set their bus addresses to the ones corresponding to the configurator.
It shows a "Bus error" however on the pump. Is there something aside from the bus address that I need to configure on the pumps themselves?
-Larry
03-07-2014 11:52 AM
Jesse,
I managed to figure out the problem. One of the cables was damaged. I am now able to communicate with the pump through the examples provided by the Labview driver.
Now I am not sure how to utilize the inputs I receive in a meaningful way. For example, I have one of the inputs set as the "ActualManualSetpoint." I change the setpoint on the HMI of the pump itself, and there are 4 numbers that do change whe nI do this. However, these 4 numbers don't correspond in any way I can see to what I am setting as the set-point. Do you have any idea how I can convert these numbers to usable data?
The pumps are Grundfos Digital Dosing DDA.
Thank you for your time.
-Larry