Discover Proface PLC for Modbus Communication

Solved!
Go to solution

Hello,

 

I want to read from and write to an industrial PLC (Proface AGP 3400) using the Modbus communication protocol. 

 

Although the PLC was successfully pinged from the command line, LabVIEW nor NI MAX weren't able to locate the device on the LAN. Hence, Modbus communication could not be established as the PLC was not recognized during configuration. To assure that the problem was not on the PLC side, a third party Modbus explorer (Modbus Poll) was installed on the same master PC to explore for Modbus enabled devices. The communication over Modbus was successfully established and registers could be read as well as written. 

 

I'm wondering, is there some configuration in labVIEW which avoids me from discovering the PLC?

0 Kudos
Message 1 of 7
(4,362 Views)

Hi,

 

Should be no problem connecting to a ModBus device over TCP.

How to do establish the TCP connection ? Do you use the NI ModBus lib. ?

 

Kees

0 Kudos
Message 2 of 7
(4,326 Views)

Hi Kees,

 

Thank you for the response.

Indeed, I intend to use the NI Modbus lib. However, I can't find the device and its items using the Distributed Systems Manager, while I can discover it when using the command line (see attached Figures) and a third party Modbus Software (Modbus Poll). So there might be a TCP connection problem in LabVIEW?

 

Cheers,

Niels

 

 

0 Kudos
Message 3 of 7
(4,320 Views)

You can use the LIB (or even create your own VI for TCP/ModBus communication) but you have to known which commands and registers/bits your device is supporting.

If want to use it in another package you have to look further. I always communicate with known ModBus devices. Since they also have dedicated command I made the VI myself for serial and TCP. 

 

Kees

0 Kudos
Message 4 of 7
(4,318 Views)

I have a list of supported registers of the PLC and when I use ModbusPoll it works fine.

However, when I try LabVIEW/NI MAX I can't even discover the device on the network...

 

Niels

0 Kudos
Message 5 of 7
(4,316 Views)

I don't think you will see this in MAX. At ethernet MAX will only discover T&M devices I think.

0 Kudos
Message 6 of 7
(4,308 Views)
Solution
Accepted by topic author NielsNicolai

I figured it out. Apparently, the I/O server has to be hosted by the localhost (or another networked device such as a cRIO).

Thanks for helping!

0 Kudos
Message 7 of 7