vi startup.exe at cFP-2010 don't starts alone

I'm developing a vi for cFP-2010. When I target cFP the program works, but when I try make startup.exe and make it work alone it doesn't.
I'm using ABCD LEDS for indicate an event, and the leds don't light..
0 Kudos
Message 1 of 4
(3,752 Views)
Did you set the start bit on the FP module? Open labview, target the FP module. Go to Tools -> Network: Options -> RT Target Miscellaneous and confirm that 'Launch Application at Bootup' is checked.

Also on that screen confirm that:
Application Path = c:\ni-rt\startup\startup.exe
Downloaded vi Path = c:\ni-rt\startup

Lastly, ftp to the FP module and confirm that c:\ni-rt\startup\startup.exe exists and has a correct timestamp.

Matt
Message 2 of 4
(3,752 Views)
Thanks for your response.
I have found the mistake. If the vi is open when I build startup.exe the exe file don't refresh in the field Point. It's easy, but not obvious.
I have another question. I'm trying to connect to the cFP 2010 by Web. I have activated the web server, but it don't works. I try
http://ipnumber/index.htm
It's the correct address?
Thanks a lot
0 Kudos
Message 3 of 4
(3,752 Views)
Greetings,

You may want to walk through a KnowledgeBase that is found on the National Instruments web site which explains using remote panels with a Real-Time target. Follow these instructions and I think you should be ok.

http://digital.ni.com/public.nsf/websearch/A4915E8E1271951086256B22005C2CAB?OpenDocument