Hi.
I am having a problem (since new) with a cFP-1804 and cFP-RTD-124.
When the unit is powered up all of the connected RTD channels display the current temperature as -30ish degrees C with a lot of noise even though the RTD elements are at room temperature. However, if the D37 connector linking the RTD elements to the cFP back plane is disconnected and reconnected (hot) all of the connected RTD channels read correctly with no noise.
I have updated the 1804's firmware to Rev 6.05 and I am running
I would appreciate your thoughts,
Paul.
PS. Rebooting the 1804 through Max or manually resetting it makes no difference, only unplugging and reconnecting the RTD's.
Solved! Go to Solution.
12-12-2007 03:58 PM
12-12-2007 04:45 PM
Hi Peter.
Thank you for your reply.
That is it exactly. I will contact NI here in Aus and organise to have it repaired.
Thanks again,
Paul.
12-12-2007 05:37 PM
Hi again Peter.
A thought…
Can you find out if the bug is caused by something simple like a noisy internal supply or something that can be fixed by modifying component values or adding additional components? If so, is it possible for us to do the repair? I ask because the unit is in operation and we will need to minimise the downtime while it is being repaired, fixing it in house would do so.
Please feel free to contact me off line to discuss. The unit is out of its warranty so that should not be an issue.
Regards,
Paul.
12-12-2007 05:48 PM