cFP-DO-401 status indicator problem

Hello

 

We use compact field point controller for one of our hydraulic test stands.

 

And cFP-DO-401 is configured for sequence of boolean operations for all the 16 channels.

 

The problem is during testing, status indicators are turned off but internally the relay still on , so operation gets failed.

 

When i checked for cause, some of transistors in the cFP-DO-401 got short circuited.

 

I want to know what might be the root cause of the failure or problem.

 

Thanks

 

Regards

Kirit

0 Kudos
Message 1 of 4
(6,556 Views)
What kind of load (voltage, current) were these digital outputs driving?  If I had to guess, I would say excessive current through the channel would have caused them to fail.
0 Kudos
Message 2 of 4
(6,554 Views)

Hi,

The cFP-DO-401 module may have been damaged by high voltage transients. When a channel of the [c]FP-DO-400/401 is damaged, the channel will remain in the ON position. Though the LEDs will turn on and off correctly, the module will always output a HIGH voltage. To prevent against this type of failure in the future, you need to place a properly selected transient voltage surge suppressor (TVSS) between V and C of the module. Refer to page 11 of the manual for this caution.

See this KB for more information.

Meanwhile the cFP-DO 401  module had a redesign in June 2008 to include the voltage suppressor. 

 

DirkW

0 Kudos
Message 3 of 4
(6,551 Views)

I would just like to add that the correct URL to the KnowledgeBase link that Dirk posted is here:

KB 4G2EC3K8: Why Does my [c]FP-DO-400/401 Have Channels Stuck in the On Position?

 