FieldPoint Family
cFP-AO-200 only puts out max current level 4.3mA
cFP-AO-200 only puts out max current level 4.3mA using fieldpoint explorer. The load is 350 ohms resistor.
Brad Whaley
LabVIEW Certified Engineer
(2,138 Views)
What is the voltage level of the external power supply you are using? The FP-AO-200 and cFP-AO-200 output load drive capability is based upon the voltage of the external supply that you are using. They each have an internal 3 volt drop. You can use V=I*R to determine the load drive capability. For example, with a 5 volt external supply, you have the 3 volt drop, so 2 Volts/ 21 mA = 95 Ohm load maximum. With a 24 V supply, you can drive the maximum rated load of 1000 Ohms. For a 350 Ohm load, you will need a minimum of a 10.5 Volt supply.
Aaron
(2,138 Views)