11-26-2012 05:15 AM
Hello everyone
I'm using the cFP 1808 Bank along with other input modules like AI-111 and AI-110 ,I recently bought a AO-200 Module to output currents in the range from 4-20 mA ,I connected the module to the bank and updated the device from the MAX Software ,then I opened the Getting Started/Analog Output.vi from the examples in the Labview 2011 in order to test the card ,the VI returns an error with the code -33180 to me ,I don't know what's wrong ,but i tested the card with the MAX and wrote values to it successfully.
Can anybody tell me what's wrong with my VI
Thanks
Solved! Go to Solution.
11-26-2012 01:30 PM
Post your VI so we can see what you are doing.
Did you read the error description for that error code?
11-29-2012 10:46 AM
I was able to reproduce your error. You have to select "All" as Field Point IO Point for this vi.