Why in my FP-TC-120 Module, the red leds are not lighting

The red indicator leds are not lighting, even if there its no TC conected, what could it happent the software works fine but the leds still turn off
0 Kudos
Message 1 of 3
(3,723 Views)
The red LED's indicate Open Thermocouple detection. However, each channel can be configured for either thermocouple (temperature) or voltage measurements. If a channel is configured for one of the voltage ranges (+/-25, +/-50, +/-100, -20 to +80 mV), Open Thermocouple does not apply so the LED's are deactivated. Use the NI-FieldPoint software to make sure that your channels are in one of the temperature modes and not in voltage mode.

Regards,
Aaron
Message 2 of 3
(3,723 Views)

THANKS AARON!! Great post... Saved me some hours!!

 

Chris