The 32800 error code can be returned in a number of situations. Depending upon which VI is returning the error code, it can be caused by a number of things.
FP Open.vi: The IAK file path is invalid The IAK file does not exist The IAK file can not be loaded (Win NT user profile problemsee: http://digital.ni.com/public.nsf/3efedde4322fef19862567740067f3cc/862567530005f09e8625679300805acd?OpenDocument&Highlight=2,fieldpoint,bridgeview ) There is a version mismatch between the FPLVMGR.dll and the FIELDPOINT.dll or between the FPCVIMGR.dll and the DIELDPOINT.dll Misc Errors
FP Write.vi The data array being input to the FP Write.vi does not contain the correct amount of information for the number of channels being target ed. For example, writing to the All channel of an FP-AO-200 (8 channels) with an array containing 7 elements of data.
"There is a version mismatch between the FPLVMGR.dll and the FIELDPOINT.dll or between the FPCVIMGR.dll and the DIELDPOINT.dll"
I am having a problem with trying to read temperatures from an FP-TC-120 module. I show values in MAX but when I try to open up a VI, no data shows up and I am getting this error. The .iak filepath is correct, all the names have been checked and re-checked. What do you do if you have the version mismatch in the .dll files? I suspect this may be the case as this computer was restored from an older computer and several versions of LabView have been installed over the years.