Hello Nacree,
From your post, I can tell that you are following most of the steps outlined in many of the knowledgebases at NI.com. It seems like you have already researched this quite a bit.
Just to make sure we are on the same page, you are trying to make an executable for another laptop that will getting data from a cFP-2010. You will not actually be running the executable on the cFP-2010 (requires Real-Time module).
What error message are you getting? Does it have something to do with invalid tags? Here is a knowledgebase that may help you fix the issue. You can set LabVIEW to look at the absolute location of the IAK file and if the IAK file is in the same absolute path as it is on the development computer, then it will work. Also make sure the versions are exactly the same in both computers.
I hope this helps.
Steven T.
http://digital.ni.com/public.nsf/websearch/22C30A6CBE1E943A862571D9006A62B5?OpenDocument