When viewing the channel 0 (count) using FPExplorer, it seems that I get around 2000CPR, instead of the 500 that this encoder is supposed to output. What does channel 0 keep track of? (Using Axis 0 only)
0 Kudos
Message 1 of 3
(3,150 Views)
Greetings,

If the device specifies that it outputs 500 CPR, then if you see 2000 in FieldPoint Explorer, this is most likely the correct result. Some encoders specifications are based only on a rising transition of one signal for one period. This would mean that both signal A and signal B are 500 Hz signals and for one period of each signal, only 1 pulse is counted. When using the FP-QUAD-510, the device actually reports 4 counts per period; the rising and falling transitions of both signals. This is to ensure that the direction of the device is known. Take a look at this document for a little more detail. Also, refer to page 6 of the FP-QUAD-510 operating instructions for illustrations. Hope this helps. Have a good day.

http://zone.ni.com/devz
one/conceptd.nsf/webmain/665470207873076386256B35007957A2?opendocument

Patrick Robinson
Message 2 of 3
(3,148 Views)
That's what I wanted to verify. Thanks!
0 Kudos
Message 3 of 3