Unexpected "Communications link watchdog timeout error"

I am using FP-1000 in conjunction with FP-RLY-422 relay unit. I configured the Watchdog timer using FiledPoint Explorer as per user manual. And it works just fine, it sets all the channels to �1� if there is no network activity for certain period of time.
But later, when I try to write to the channel, again, using FiledPoint Explorer it sometimes gives me "Communications link watchdog timeout error". I have to click �Write� button again to get the value written.
Is there any workaround other than just send each command two times?
0 Kudos
Message 1 of 2
(2,890 Views)
This is expected behavior for the module. The communications link watchdog is a safety feature that allows you to set the outputs to known values when communications with the controlling system are lost. Thus, when communications are resumed, there is a need for the FP-1000/1001 to let the control system know that it had gone into watchdog mode, the first command it receives following the watchdog timeout, generates the response string "N06" (see FP-1000/1001 Progammers Reference Manual page 2-3) and ignores the command. Subquent commands that are received will execute normally (until another timeout occurs). What you can do in your code is to look for the "Communications Link Watchdog Timeout Error" to know when the system went into the watchdog mode. At that po
int, the system outputs may be out of synch with what the computer thinks they are (since the FP-1000 will change the states of any channels that have the watchdog enabled), so you can then initiate some sort of re-start/re-synch sequence in your code.

Regards,
Aaron