A problem may be that the resource/device/item names that are configured in MAX, and/or the IAK file name may be different on the target so the EXE may be trying to access a non-existent item.
Also, try updating the FieldPoint Driver, using the following options:
Product Line: Distributed I/O –
FieldPoint
Software: NI-FieldPoint
Software Version: 5.0.1
Operating System: Select your operating
system.
After doing this, make sure to update your FieldPoint driver on the target as well.
Please try to create an example that only reads from the AI-100 module and see if you are able to get any data from that. Run it both as a VI and as an executable. Also, can you please clarify what you mean by fails to work? Do you mean that the data is incorrect, nothing is being read, the values are all zero?