PT1000 and RTD-124?

Hello,
I found this in the operation instructions for the RTD-124 module:
The [c]FP-RTD-124 has built-in linearization algorithms for
platinum RTDs of either 100 or 1,000 Ω nominal resistance,

I'd like to configure the RDT-124 module to measure PT-1000, but it seems, that this sentence is wrong. Am I right?
Thank You
Olli
Message 1 of 8
(10,006 Views)

Olli,

I'm not sure what you think is wrong.  A PT-1000 is a 1000 ohm platinum RTD.

0 Kudos
Message 2 of 8
(9,997 Views)
Hello Centerbolt,
thanks for the reply. Yes, that's why I'm asking. In the specifications of the RTD-124 module you'll find nothing about 1'000 ohm. The direct resistance measurement range is limited by 400 ohm.  In the MAX channel configuration I can chose between 6 different linearisation coefficients for PT-100 but nothing about PT-1000.
I will simply connect one PT-1000 and see what happens compared to a PT-100 measurement.
Ciao
Olli
Message 3 of 8
(9,986 Views)
OK...the practical test showed the following results:
PT-1000 connection -> open RTD detected (= out of range)
PT-100 connection -> shows linearised temperature correctly

I checked both RTDs with an ohmmeter before I connected them to the RTD124 module.

Message 4 of 8
(9,985 Views)

Olli,

I see what you are talking about.  Any mention of a PT-1000 in the RTD-124 documentation must be a mistake.  You may want to inform NI of the mistake.

0 Kudos
Message 5 of 8
(9,980 Views)
Hi Centerbolt,
sorry for my unclear explications above (german native speaker :-). I'm waiting for a call-back from NI to report this. The technical support in my region seems to be quite busy today!
Greetings
Olli
Message 6 of 8
(9,978 Views)
Olli,
 
Your English is pretty good by my book.
 
I wonder if NI based the documentation for the RTD-124 on the documentation for the RTD-122 and just forgot to delete the reference to the PT-1000 during the edit process?  That's how mistakes like this usually happen. 
0 Kudos
Message 7 of 8
(9,975 Views)

Hi All,

 

I hope your all well.

 

Just to let you know, I just had a customer with the same issue.

 

There has been a CAR 46008 produced on the issue, it certainly does seem like an error in the operating manual.

The Spec Sheet shows RTD-122 module supports both 100 and 1000.

 

Best of Luck,


Kind Regards 

Kind Regards
James Hillman
Applications Engineer 2008 to 2009 National Instruments UK & Ireland
Loughborough University UK - 2006 to 2011
Remember Kudos those who help! 😉
0 Kudos