12-03-2007 12:19 PM
12-03-2007 12:35 PM - edited 12-03-2007 12:37 PM
12-03-2007 12:47 PM
Matt,
Thanks for the reply.
1) I have double checked that the TC wires are the same throughout but may check again to be sure and will get someone to double check.
2) The wires are physically touching.
3) I am using a CFP-CB-3 I must of omitted that peice of information. Is there anything special I need to do withthe internation CJ I did the calibration mentioned in the KB article I found?
4) Unforutnately, this requires uninstalling most of my hardware from the box and is very undesirable but if I do not see any results I may have to result to this eventually.
5) No the temps in MAX and application do not agree iether. The funny thing is when I initially installed everything I tested all of my devices and the thermocouples read very similar readings. When I came back the next day and the refridgerator had been turned on (thus the rooms where colder) I got this weird readings.
I spoke with the company I purchased the thermocouples from and was told to check the voltage readings from the thermocouples manually and compare with what is read by the application. I figure I will do that today. I figure while I am manually checking each TC I will also double check (again) that each wire is connected proerply. I hope it is a wiring isssue. I figure if I cannot get anything working after today I am going to call NI and see if they can help.
Any other thoughts/suggestions.
12-03-2007 01:20 PM
12-03-2007 01:50 PM
12-06-2007 11:42 PM
12-07-2007 06:03 AM
12-07-2007 06:17 AM
Matt,
How cold is it where the FieldPoint unit is located? It is roughly -30C...It is located in an enclosure and other than the TC problem everything is running fine. I could try changing the temp in the reefer to a warmer temp and see if performance is affected.
Have you tried unplugging and re-plugging each of the TC-120 and CB-3 several times since the unit was placed in the cold environment?No do you think that would help...I will try that this afternoon.
Are the CJ and sensors reading properly with MAX, or with the short, test sensors? I am unsure if the CJC is reading proerply. I do not know the actual temperature in the compartment but from what I can tell it is in the ballpark of the refridgerator's set temperature. I have not tried connecting another TC I planned on doing that this afternoon (this is my second job). My thermocouples are attached to shielded & twisted thermocouple wire (from Omega). The wire runs any where from 10' to 40' to the FP module. In th e"control" room where it is -30C they terminate to the FP module. Last night I warmed up the wire in the control room and notice that my temperature readings had changed. Do you think the wire itself could be the problem? Now I plan on attaching a TC to one of the open channels and checking the readings. Then I was going to check the the temp of the TCs in each room (comparing the measurement with an independent temperature device). I really hope it is not the wire b/c that woudl be a real pain trying to run it again!
Thanks for all of your input Matt!
12-07-2007 06:43 AM
12-07-2007 07:03 AM
Where are the shields connected? That may be one of the problems I did not connect the ground to the ground lug...I will do that for all of the sheilded wires.Do you think that could cause that big of a problem? (And all of the EE's shriek simulatanesouly) They are not connected to anything on the sensor end.
I doubt the wires are bad as well. That is a good idea about running a wire in parrallel.