Hi Presario2100,
There are documents that may help you along. Please see:
What Ports Do I Need to Open on My Firewall for National Instruments Software Products?
Using Lookout, LabVIEW DSC and Network-Published Shared Variables with Firewalls
As for your timestamp question, let me look into this a bit more. What you described is expected behavior, but there may be a work-around.
08-15-2008 05:57 PM - edited 08-15-2008 05:58 PM
Hi Presario2100,
In order to obtain an updated timestamp with each FieldPoint Read, you should use a Flat Sequence structure. In the same frame as the FieldPoint Read, use a Get Date/Time In Seconds node.
The program obtains a fresh Timestamp each time the FieldPoint Read VI is called.