Field point 120 configuration cold junction

I use field point explorer,
The module tc 120 has 8 channel, 7 are for TC readings and the 8th is the internal temperture for the cold junction compensation.
I need configure this channel but I don't find settings in the Field point explorer for change compensation type and range(Celsius instead of Kelvin)
 
Thank you for your helpSmiley Very Happy
0 Kudos
Message 1 of 2
(2,863 Views)

Hi delpitik,

the module FP-TC-120 ha s 9 channels, 8 for TC readings and the 9th one reads cj Temperature.

It's possible to set the range configuration of the cj Temperature channel following the steps:

  • go to the Channel Configuration Tab in the FP-TC-120 page of the Remote System on MAX
  • select "Type 2: Analog Input #2" instead of "Type 1: Analog Input" from the menu above channels selection
  • change Data Configuration Range to "-50 to 85 Celsius"
  • Apply and Save the configuration

I hope this helps you.

MarcoC