03-19-2008 09:52 AM
03-19-2008 02:31 PM
03-19-2008 04:07 PM
03-20-2008 08:10 AM
03-20-2008 09:47 AM
03-20-2008 09:58 AM
03-20-2008 07:04 PM
BR549 wrote:
Ok, I have another question(s).(1) I am not sure which terminals to use to connect a "K" Type thermocouple wire. + to V-in and - to COM ?(2) I am a little confused on the instruction you gave me on connecting the load cell, being that I am using an external power supply. Reference Figure 5. of the manual.(3) When I open MAX, Data Neighborhood and click add new, I am only able to add a new virtual device. Is this correct or should the devices connected appear?Thanks for the help Ravens Fan!
03-25-2008 11:05 AM
"3. Jeff gave you a little more detailed explanation than I gave before. You need to find the remote system by opening the bottom Remote Systems part of the tree. Once you find the fieldpoint, then you select find devices. This will make all the modules appear at the top of the tree under Data Neighborhood."
I assume that we are talking about doing this in MAX? Where in MAX is the "remote systems" part of the tree? Every time I add a new device to Data Neighborhood it reads Invalid Configuration when I try and test the load cell.
Also, should the range in FieldPoint for the transducer I am using be set to "0 to 10.4 volts"? 10 volts would be the input for the transducer, but the output is 2 mV/V.
Thanks!
03-25-2008 01:52 PM - edited 03-25-2008 01:58 PM
Yes. In MAX. See Attached
1. Open Remote Systems.
2. Select remote system, pick Find Devices.
3. Look at what was added to Data Neigborhood.
4. Pick a module.
5. Hit Start to see the current data.
I myself would use a strain gage module in your application, I haven't tried setting up an ordinary analog input module to read a strain gage bridge. I would set a range that meets or slightly exceeds +/- 20mV since you have a 2mV/V signal with a 10 V source.
03-25-2008 02:30 PM