02-23-2011 11:27 AM
Does cFP-TC120-8channels need PIN 20 of BackPlane?
I have broken the PIN Number 20 of Slot1 of the the BackPlane, but the cFP-TC120-8 works fine in that slot.
Could there be any impact?
Thank you.
Solved! Go to Solution.
02-24-2011 06:51 PM
I am going to look into this and post an answer for you soon.
03-01-2011 04:57 AM
Any ideas?!
03-01-2011 10:09 PM
The first line on page 4 of the manual for this device states "The COM terminals of all the channels are internally connected and are connected to the terminals labeled C on the terminal base." Therefore, the cFP-TC120-8 will work fine in that slot with #20 missing. You can use any of the other COM pins or the C terminal connection in the terminal block (there are two of them). Pin #20 is COM (ground) for channel 1.
http://www.ni.com/pdf/manuals/373344a.pdf
03-02-2011 02:40 AM
Thank you Patricia!