12-02-2011 01:43 PM
Hi Tim,
I was finally able to get ahold of a cFP 2100 and test it out. I saw that same behavior you did.
You should be able to run I/O Trace and see the VISA call that searches for the available ports. I'll do the same and see what I come up with, but I'm suspecting that you are correct and this is a bug.
Have a great day,
Chris V
12-04-2011 06:17 PM
Thanks Chris,
While you are at it maybe you can see if you can find out why FP Close doesn't work (not included in the library) in later versions.
Kind regards,
Tim L.
12-05-2011 03:54 PM
Hi Tim L.,
I'm surprised that you did not see the FP Close function in LabVIEW. I still have it in LabVIEW 2011:
Is there something else more specific that you meant by "doesn't work?"
Have a great day,
Chris V
12-05-2011 06:28 PM
The vi is there but during deployment is says something like --Cant find funcuntion vI_........---
It appears that it hasn't been included in the fieldpoint library (the one installed via MAX)
Tim L.
12-06-2011 01:35 PM
Hello Tim,
This is Andrew Brown, an Applications Engineer from National Instruments. To further clarify your hardware and software setup:
1. What version of the FieldPoint driver are you working with?
2. Which devices does this problem occur with? (cFP 2100, 2200, 2220)
This type of a problem has been documented with CAR 202774. The problem is limited to certain versions of the FieldPoint driver with cFP-21xx and cFP-22xx series controllers. If you are not working with FieldPoint 6.0.9, I recommend upgrading to it as a solution. If this is not possible, versions 6.0.7 and 6.0.8 also resolve the issue.
Regards,
Andrew Brown
12-06-2011 06:17 PM
Andrew,
As per the first 3 lines of my first Post:
Problem #1 - Missing Com port occurs on cFP 2100 with 6.0.8 and more recently 6.0.9
Problem does not occur on cFP 2200 and cFP 2220 running 6.0.8 and 6.0.9 although it does require that the vi is run and then refresh is used from the combo box before available channels can be seen.
Problem #2 - FP Close failed on a cFP 2220 using 6.0.8. I have not tested it on 6.0.9, I had given up on this one since I had no further correspondance from NI after I reported it.
The cFP is the low cost, extended temperature range, core of our systems and has been performing well doing it's current job.
Unfortunately it has been resisting my attempts to add features and functions to our past, present and future systems.
/Rant/
I understand that older devices (such as the cFP 2020 and cFP 2000 that I am using to stop by door from swinging shut) are no longer supported by NI, this is business.
I am disappointed that the cFP 2100 and some some functions (Loop parellelism, Object oriented, FP Close), are badly supported. It has cost me days investigating them without resolution.
I understand that NI is obseleting cFP's in favor of cRIO (At twice the price for my application) I assume that the degraded functionality is a by-product of less care being taken on a legacy product.
Am I likely to encounter much of the cFP code in the cRIO environment that I am planning to migrate to?
/End Rant/
Kind Regards,
Tim L
12-07-2011 04:37 PM
Hi Tim L.,
Did you ever get a chance to test this out on LabVIEW 8.6?
I tested this with a 2120 as well and it worked fine, so the problem is not with Pharlap ETS controllers, but specific to the cFP 2100. You are probably correct that this is a bug.
In response to your other comments, National Instruments still provides support for Compact FieldPoint and legacy FieldPoint. Legacy FieldPoint has been End-of-Lifed, but Compact FieldPoint has not been End-of-Lifed, so it will be supported for the foreseeable future.
Have a great day,
Chris V
12-07-2011 06:17 PM
I didn't test it with 8.6 as we have obseted it.
I am surprised to hear it worked on a 2120 - I would have assumed that tis would have been based on the same operating system.
Kind regards,
Tim L
12-08-2011 09:01 AM
Hi Tim L.,
I tested in 8.5.1 and FieldPoint 6.0.8 with no luck.
This was reported to R&D (#328346) for further investigation. Unfortunately, I did not find a viable workaround for this bug.
Thanks for the feedback!
Chris V
12-14-2011 05:08 PM
Hi Tim L.,
Good news! I have a possible workaround from R&D.
1. FTP to the controller and copy the /ni-rt/system/niserial.ini file to your computer
2. Delete the
NonPnpDevice2
NonPnpDevice3
NonPnpDevice4
sections from that file
3. Copy the niserial.ini file back to /ni-rt/system/ (replacing the old file)
3. Reboot the target
Let me know if this works!
Have a great day,
Chris V