The two DO channels are both connected to 24vdc small 2way solenoid valves (10w coil).
The part I don't quite understand yet, is the fact that I record data every 60s on an HMI connected to the cfp-2110. During this time period of over 24hrs, I recorded that the digital outputs (ch 5&6) were held on. This log is stored on the HMI, in which I use shared variables and data sockets. If the outputs were held on by some external means, would labview still record the outputs as being on?
12-19-2007 07:14 AM - edited 12-19-2007 07:15 AM
Do you have flyback diodes installed across the coils of the valves? Diode needs to be installed as close as physically possible to the coils.
My guess would be that a large pulse is being produced when the coils are being de-energized. Such a pulse could then cause your problem.
12-19-2007 09:38 AM