09-20-2007 08:14 AM
09-20-2007 09:56 AM
Hi Tim,
Though you can start both devices at the same time, we currently don't support advancing records on multiple devices at the same time. Can you please give more details about your setup, connections and what you are trying to accomplish? Seems like your setup is doing both acquisition and generation since you refer to a script. We may be able to work out a solution using a single record case.
Onome Ufomata
Software Engineer,
High Speed Digital IO
09-20-2007 06:52 PM
09-21-2007 09:10 AM
Hello Timothy,
You cannot use one script to run three separate boards. Once you develop the script, it will actually be downloaded to the physical board. However, there might be a way to synchronize all three boards for your application. If you export the clock on one of the boards to the other two, then they will be acquiring and generating at the same rate. The next step is to use triggers to synchronize your boards. This method will require you to develop a complex script for each board. Now all three boards will be synchronized because they are using the same clock and they are advancing using the same triggers.
09-21-2007 10:55 AM
09-21-2007 10:57 AM
09-24-2007 06:12 PM
You will have impedance mismatch, since the three PXI-6561 STROBE inputs are going to be in parallel like you said, giving you an impedance of 33 ohms. If the DUT output is 50 ohm you might try it. If it does not work then you will need a Bus LVDS, LVDS driver, and it will depend on your DUT device specifications. But at the end what you need to accomplish is be able to source approximately 3.5 mA to each of the Strobe Pins.