04-17-2013 01:57 PM
Hi all,
I have a quick question regarding the use of a NI 9476 to drive a relay, which is a sourcing DO module that can take anywhere from 6V to 36V and source 250 mA/ch.
The NI 9476 will be powered with an external 20V power supply (Unfortunately, this is the only one I have) and I will be driving two relays using one output from the NI9476. The relay I'm using is: G2RL-1A-E DC12, which has a 12V coil voltage and a 33.3mA coil current resulting from a 360Ohm coil resistance.
Since 20V output of the NI9476 is much greater than the 12V coil voltage, the relay will draw too much current and kill itself. I was wondering whether I could get around this issue by just adding a 250Ohm resistor in front of the relay and stepping the output down to 12V. (250Ohm resistor + 360Ohm relay coil resistance).
Also, I read that the NI9477 (a sinking DO module) requires the use of a flyback diode when driving relays. Does the 9476 have to have similar provisions?
Thank you!
04-18-2013 01:15 PM - edited 04-18-2013 01:19 PM
lets make this simple...just use a LM7812 with a ULN2003( which has 'flyback diode' protection built in)...
04-18-2013 07:23 PM
Thank you for the answer! Interesting....
In this application, wouldn't I need a sinking DO? (Meaning that I would need the NI9477 isntead of the NI9476).
Also, what are the benefits of this application instead of my resistor? (Out of curiosity)
Thanks!
04-19-2013 02:17 PM
Thanks!
yes, tie the gnds together with your Daq
benefits are your current load does not effect the regulated voltage, on the other hand..it would effect your resistor drop
09-01-2021 09:05 PM
According to the Getting Started Guide, you need a Flyback Diode. https://www.ni.com/pdf/manuals/373964h.pdf