Digital I/O
Power requirement for NI 9266 @ 24VDC
What is the total power requirement for NI 9266 @ 24VDC from external power suppluy and from chassis
(1,398 Views)
Details are available in the specifications document - https://www.ni.com/pdf/manuals/376325c_02.pdf
Santhosh
Soliton Technologies
(1,367 Views)
Hi Santosh,
Thanks for ypur reply, I have gone through the manual/Datasheet. That means from the chassis it draws 230mW for all 8 channels.
From external power source it draws 3.1 Watt maximum with for all 8 channels.
I need to consider both power supply current for calculation
Hope this understanding is correct. please confirm.
The same way for other IO cards also to be calculated?
Regards
Shivaraju MB
(1,342 Views)
Yes. That is how I would do that.
Just curious, why are you interested in individual module power consumption? are you going to run this off a battery?
Santhosh
(1,338 Views)
Thank you for your reply,
No. Notrunning on battery!
I am using NI cRIO 9056 Chassis (8 Slots) long with 8 different IO Modules (AI/Ao/Di/Do/Serial)...so need to calculate the total power supply required for the entire system.
Apart from the above system, I have external relay modules/Boards (of third Party) to drive some loads (like Solenioed/Contactors........)!.
Thank you.
Regards
Shivaraju MB
(1,332 Views)
