10-26-2021 02:35 AM
What is the total power requirement for NI 9266 @ 24VDC from external power suppluy and from chassis
10-26-2021 08:09 AM
Details are available in the specifications document - https://www.ni.com/pdf/manuals/376325c_02.pdf
10-27-2021 03:48 AM
Hi Santosh,
Thanks for ypur reply, I have gone through the manual/Datasheet. That means from the chassis it draws 230mW for all 8 channels.
From external power source it draws 3.1 Watt maximum with for all 8 channels.
I need to consider both power supply current for calculation
Hope this understanding is correct. please confirm.
The same way for other IO cards also to be calculated?
Shivaraju MB
10-27-2021 09:38 AM
Yes. That is how I would do that.
Just curious, why are you interested in individual module power consumption? are you going to run this off a battery?
10-28-2021 04:09 AM
Thank you for your reply,
No. Notrunning on battery!
I am using NI cRIO 9056 Chassis (8 Slots) long with 8 different IO Modules (AI/Ao/Di/Do/Serial)...so need to calculate the total power supply required for the entire system.
Apart from the above system, I have external relay modules/Boards (of third Party) to drive some loads (like Solenioed/Contactors........)!.
Thank you.
Shivaraju MB