DAQPad-6508 Digital I/O Pulled-low mode Selection Problem

Hi,
I have a problem to use that DAQPad as pulled-low mode rather than pulled-high mode.Basically that DAQPad-6508 has a front panel switch to change the power-up state selection for 96 channels.
But jumperd the switch to pulled-low mode to use 96 channels, both DI and DO will not work properly. DI does not get any state change, and DO works like pulled-high mode.
Insted jumperd to pulled-high mode, both DI and DO work fine at this time.
Why the pulled-low mode does not work properly?
Is there any difference between line connection as to the mode selection?
0 Kudos
Message 1 of 2
(3,731 Views)
Yes, there is a switch that should set all the lines to either high or low in the power-up state. The switch uses a 100 k resistor pulled up to either 5 VDC or GND. Are you using the Measurement & Automation Explorer Test Panel for the DAQPad-6508 to verify the power-up state as well as a multimeter? You can try to manually pull high or low lines using the instructions on page 3-9 of the DAQPad-6507/6508 User Manual to see if that gives the correct response. The manual is located at the http://www.ni.com/manuals pages.

Regards,

Geneva L.
Applications Engineering
National Instruments
http://www.ni.com/ask
0 Kudos