I only had a pretty brief look on a system that could open your LV2021 code, and have one small nitpick.
Your example overconstrains the execution timing. The DAQmx Read functions will already pace the iteration rate, only returning when a sample is available. With your default rate of 1 S/sec, the loop will iterate at 1 Hz. But then you have an *additional* timer function that waits for a msec multiple of 1000 which is *also* trying to make the loop iterate at 1 Hz.
The tiny nitpick of a problem is that the DAQ device and the system clock won't agree on exactly how long 1 second is, there will be some microseconds of discrepancy which could potentially accumulate. It's probably not a *real* problem in your posted example unless you run for a very long time. But if someone starts making mods so that the 2 timing constraints no longer nearly agree, they could get into some trouble.
I just wanted to warn anyone who finds your solution that they generally shouldn't have both DAQmx and the msec timer trying to constrain the loop rate at the same time. I'd recommend putting DAQmx in charge and removing the msec wait function.