10-08-2015 05:01 AM
Hi,
Got a running system with an SCXI-1104C module. I now have some measurement errors I never had before.
As a spare unit I have a SCXI-1104 (no "C")... Is it direct compatible with the system ? Can I exchange
the 1104C for 1104 to eliminate multiplexor fault ?
//Beck777
Solved! Go to Solution.
10-09-2015 06:57 AM
Hi Beck777,
You can find the manual for both the SCXI-1104 and the SCXI-1104, at the link below:
http://www.ni.com/pdf/manuals/322147b.pdf
If you read the common questions it explains that the only difference between the two is the cutoff frequency of the filters. It also says that NI-DAQ version 6.7 or later is required for the SCXI-1104C whereas you only need NI-DAQ version 6.5.1 or later for the regular 1104. If you have the correct version of NI-DAQ it should work but be wary of the cut off frequency. You may end up with a lot of noise on your signal.
Regards,