Software Trigger set by alarm is not seen in Log start/stop conditions

AHH the frustration....

 

 

So it seems to me that in SignalExpress you should be able to create an alarm Action  when a signal reaches a certain level to generate a software trigger.  Then you should be able to trigger a log start condition on this software trigger.   Unfortunately, this does not work for me.  Can anyone confirm?

 

My intent was to have like 3 or 4 alarms that all generated  software trigger A.  Then when the Alarm turns off, It would Trigger B

Then my start condition for the log was trigger A and my stop condition was trigger B.

 

I think that this is a bug, or this hasn't been implemented into signalExpress yet.

 

Your thoughts?

Ben Yeske
0 Kudos
Message 1 of 2
(5,576 Views)

Hi, Ben Yeske.

 

The functionality that you're looking for can be found in the Limit Test in Signal Express (Analysis»Test and Compare).  You can use two Limit Tests:  one can act as software trigger A and the other can act as software trigger B.

 

Let me know if you need any more help.  I hope you're having a great day!

Regards,

Sara Lewandroski
Applications Engineer | National Instruments