01-15-2015 11:00 AM - edited 01-15-2015 11:02 AM
I am usig 1520 for bridge type pressure sensor data acquisition.
I have a requirement for potentiometer type pressure sensors. The sensor is a potentiometer that needs 5V exciation.
+---------------- Exc+
| |<-------------- O/p+
+---------------- Exc-
I was wondering if I could use 1520 for interfacing with such sensors?
I am hoping I can short P- and S- lines and connect to Exc-. P+ would be Exc+ and S+ would be O/p+.
The resistance between Exc+ & Exc- is of the order of 1-5 kOhm. So the current drawn from the excitation supply is of no concern for the 1520, I believe.
Can I do this with the 1520?
09-08-2016 09:51 AM
Hi there,
I have a similar requirement. Do you manage to get results from the setup?
Shazlan
09-09-2016 10:50 AM
Hi
We haven't tried it out so far since our system requirements were changed later. But my guess is that it should work fine.
02-10-2017 12:03 PM
This can be done.
Your pinout arrangement is correct as you describe.
You'll want to configure the sensor as a "Full-Bridge with Excitation". Set the Vex to 5Vdc in software. Also, a custom scale will probably be necessary unless you want to post process the output voltage to pressure units later.