NI 9217 with PT100 resistance thermometer connection details

The Pt100 sensor is combined with the transmitter in one unit that's what the SEM206P is, and I have both 9208 and 9217 modules

0 Kudos
Message 11 of 16
(3,244 Views)

Apologies but I am struggling to find an actual picture of the full unit, it is combined with a Pt100 sensor with the transmitter internally connected, so in effect all I have to connect up are the positive and negative terminals to somewhere??

0 Kudos
Message 12 of 16
(3,242 Views)

Again apologies for my mistake, the SEM206P is not the total unit, I have a SEM206P which is connected to a Pt100 sensor in a combiened unit with the postive and negative terminals to connect.

 

Really should read what I am writing before I post.

0 Kudos
Message 13 of 16
(3,241 Views)

Than you have 2 Options, both of them will work.

 

1) Using PT100 + Transmitter : Use NI 9208 : Connect (+) coming from the SEM206P to Vsup of NI9208 (19), connect (-) coming from the SEM206P to AI0 of of NI9208 (1) . Then use the sample program of NI 9208.

 

2) Using PT100 only : Use NI 9217 : Remove the transmitter connections of the PT100 sensor, then you will have 3 wires: Red, white and white. Connect Red to RTD0+  (1), connect white to RTD0- (2), connect second white to COM (3) . http://www.ni.com/pdf/manuals/374187c.pdf

Message 14 of 16
(3,240 Views)

All working fine now, just connected the Pt100 without the transmitter wired in.

 

Thanks again for your help tcanger, greatly appreciated.

0 Kudos
Message 15 of 16
(3,228 Views)

not to mention, we usually struggle at the most simplest point, and people called experts are those who failed the most.