module 9222 is not shown on NI Distributed Manager

 

first installation of 9082 compact Rio system , 8 cRio modules are installed in the following order (from 1:8)
9205,9222,9215,9203,9263,9401,9375,9870 , NI Distributed Manager 2012 can review and detect all modules EXCPECT module
number 2 (9222) , please review attached configuration.
Best Regards
MyKat

Download All
0 Kudos
Message 1 of 2
(3,001 Views)

In this case the problem is that this particular module is not supported for the 2012 version of the software in  the Scan Interface mode, which is required for the Distributed System Manager, you  can check this by looking for this module on the following website.

 

http://www.ni.com/product-documentation/10622/en/

 