01-18-2015 01:09 PM
All,
I have a cRIO-9068 that I am trying to use the scan mode for. I have intalled all the latest drivers and software as explained. However, when I set my chassis to scan mode and then select deploy all, I recieve this error on my chassis and all of my modules:
"The current module settigns require NI Scan Engine support on the controller. You can use Measurement & Automation Explorer (MAX) to install a recomended software set of NI-RIO with NI Scan Engine support on the controller. If LabVIEW FPGA is installed, you can use this module with LabVIEW FPGA by adding an FPGA Target Item under the chassis, and drag and drop the module onto the FPGA Target Item."
Has anyone experienced this or know why labVIEW won't recognize that the software is installed on my cRIO or is it not being installed correctly?
Solved! Go to Solution.
01-19-2015 08:47 AM
Hi George,
Can you see the NI Scan Engine as an installed component on your device in MAX?
Regards,
AGJ
01-19-2015 09:53 AM
01-19-2015 10:03 AM
George,
Where are you seeing that? Would you send us a screenshot?
Thanks.
AGJ
01-19-2015 10:50 AM
AGJ,
Thank you for the image. I was seeing a green arrown next to all of my microchip images and it looked like that meant the software wasn't really being installed. I formatted my cRIO and did a custom install. My issue was that I had both labview 2013 and 2014 installed and the cRIO was installing conflicting software versions. After doing a custom install and choosing only the 2014 versions, my image now looks like yours!
01-19-2015 11:01 AM
Great!
Regards,
AGJ
02-02-2015 01:17 PM
I am getting the same error message with cRIO 9030 whenever I try to deploy an I/O module on the target. I have verified in max that NI Scan Engine 4.3 is installed on my cRIO target.
02-02-2015 04:48 PM
So I found that the target's Scan Engine was in Configuration mode. After placing it in Active, I was able to deploy all of the modules on the cRIO target. However, now I cannot deploy any of my modules on my EtherCAT NI 9144 racks regardless of which scan mode I place the Scan Engine. I verified that I have all software on the cRIO target I need. I was also able to find the EtherCAT slaves and their modules on MAX and I was able to add them to the project. The problem I am having is being able to deploy them. I have gone through the procedure outlined in the manual provided with the EtherCAT racks and the following link with no issues: http://www.ni.com/white-paper/10555/en/
The top LEDs on the EtherCAT racks are solid yellow and the bottom are solid green. Does anyone know why I may be having this problem?
02-03-2015 07:00 AM
02-03-2015 07:06 AM
I switch by right clicking the cRIO > Utilities> Scan Engine Mode
I just finished formating the cRIO, re-installing software, discovering cRIO and EtherCAT modules in MAX, adding cRIO and EtherCAT module to the project, put the scan engine mode in "Configuration", and selecting "Deploy All" by right clicking the cRIO and it was able to deploy all modules, including those on the EtherCAT remote racks. Did I switch between modes incorrectly? Not sure why it works now except that I must have done something to the settings.