Unable to view Analog IO channels in Veristand Profile Editor for Data Logging

Solved!
Go to solution

I am using VeriStand 2016 and new to this software. I had defined analog channels 'Motor Open' and 'Motor Close' in my system definition file as shown in figure 'LoggingProfileEditor'.  I want to log those channels from a VeriStand RT sequence editor but am unable to view the analog channels for selection in the drop down list under channels in the test step 'Channel Group' as shown in figure 'Logging Profile Editor'.

 

Kindly let me know is this the method for logging analog signals from RT sequence editor. If this is correct, am i missing any additional configuration for making the channels visible under the Channel Group for selection.

Download All
0 Kudos
Message 1 of 2
(2,537 Views)
Solution
Accepted by topic author vravi

I was able to view individual channels once I updated the Sample Mode of the Analog Device as 'Single-Point' in the System Definition File.