11-11-2005 03:33 AM
11-11-2005 09:47 AM
11-11-2005 10:02 AM
Test 1 | Passed |
Begin Sequence: Test 1
(C:\Dokumente und Einstellungen\wernsmad\Desktop\Sequence File1.seq)
Step Status Measurement Units Limits Low Limit High Limit Comparison Type Action Error Error Message: [Error Code: 0]
Maybe this screenshot helps to understand my problem.
Thanks for your help
11-11-2005 11:13 AM
Alligator,
Could you attach a simple sequence file presenting this error.
I would like to check your step settings.
Regards.
Antonio Lie.
11-14-2005 02:04 AM
11-14-2005 02:20 AM
11-15-2005 11:43 AM
Alligator,
Ray is right.
If you want to set the status of the step to error you need to set the following properties:
Step.Result.Status = "Error"
Step.Result.Error.Code = Specific error code. (0 = user defined error code)
Step.Result.Error.Msg = Desired Error Message.
Step.Result.Error.Occurred = True.
This will generate a run-time error message containing your error code and message and will cause the status of the sequence call step to be Error.
Check attached sequence file.
Regards.
04-04-2006 09:33 AM
Daniel or anyoneelse,
I am having a similiar problem. I am trying to get the report to say failed when there are errors not just failed steps. Was there ever a solution to this problem? I also dont have the ignore error settings set to true.
Brian
04-04-2006 02:49 PM
Brian,
If you set RunState.SequenceFailed = True then the overall Status in the Header will be set to Failed.
Ray Farmer