10-07-2015 07:09 AM
we are using a NI 9219 module for current measurements. We have 2 position sensors and 2 flow meters connected to one module. We have 3 systems containing 3 modules. Normally everything works fine, but after a restart of a system there is a chance you get the maximum reading of an input (25 mA). After some resistance measurement's on the input I discovered that the module switches off his current measurement (shunt) resistor. Ofter some while the resistor is back online again, but we are certain that the sensor aren't giving this value so I started to dig in the module. Thanks to NI support we established the following:
So to avoid this from happening, or to get everything going again the sensors should be disable giving the protection circuit the chance to recover and put the 30 ohm resistor back in place again. For us this means that we need to design this in the control system since all three locations are very remote.
With other modules (like the NI 9203) the resistor is never switched off. So with other applications we didn't take a reset circuit in account. So we ever implemented it this way, but should it normally be this way? So if you reset (software reset or hard reset) your system is it common to switch off your sensors, then reboot your system and after reboot enable your sensors again?
I know this isn't really a problem question, but I'm curious if it is just us who missed something.