I am having a problem in connection of NPN hall effect sensor 24VDC 25mA to NI9203
 (http://ie.rs-online.com/web/p/products/7659321/?cm_mmc=IE-PPC-_-google-_-3_IE_EN_BM_A_and_C_Exact-_-...
Could not get an output in Labview graph.
Any ideas or wiring suggestions.
Cheers,
Zilvinas
(286 Views)
Re: NI 9203
You have a 20mA analog current input modul, and a NPN (open collector) digital  output sensor.
You need a power supply (5-24V) and a pull up resistor.
Power the sensor, share the COM with the 9203, connect the sensor output to a AI and add a pull up resistor of
R= U_supply/20mA ~ 1.2kOhm
(well, missed the input burden resistor .. R= U_supply/20mA -138 Smiley Wink )
from AI to the powersupply of the sensor.
The sensor output will 'shortcut' the current to ~0mA , if you want to make it ~ 4mA add another resistor of ~20 Ohm between sensor output and AI (keep the pull up between AI and U-supply).
Greetings from Germany
Henrik
LV since v3.1
(236 Views)
Re: NI 9203
Thanks Henrik,
There are 2 resistors inside 9203 already(see picture attached). Does it required additional resistor?
Zilvinas
(216 Views)
Accepted by topic author Zilvis1972
04-12-2017 07:03 AM
Re: NI 9203
No, there are 8 resistors with 138Ohm, each channel has one to measure the current Smiley Wink
here is a quick draft:
R3 = 1.2k limit the current to ~20mA (~17.94mA) , this resistor dissipates ~0.4W , so it should be rated at least 0.5W , better 1W  (common is 0.25W or less with SMDs Smiley Wink )
If you (or someone with EE knowledge in your company) only has .25W resistors on stock, you can use four 1.2k resistors (two pairs parallel and these serial) ..
Henrik
LV since v3.1
(194 Views)
Re: NI 9203
Thanks Henrik,
Will give a go with that.
Cheers,
Much appreciate
Zilvinas
(188 Views)