Multifunction DAQ

cancel
Showing results for 
Search instead for 
Did you mean: 

NI 9203 current sensing module

Hi I have a 9203 module that's is a current sensing module and it's an 8 channel module, I am measuring a 4-20 ma pressure transducer from a compressor which is in this module and works perfectly in Labview, and I would like to have a different device, measure that same current and effectively Y splitting the cable. How can I do that?

0 Kudos
Message 1 of 2
(2,884 Views)

Hi jehad10,

 

Here is a good document that explains and gives examples on how to set up transducers and devices in a 4 - 20 mA current loop:

 

Fundamentals, System Design, and Setup for the 4 to 20 mA Current Loop

http://www.ni.com/white-paper/6940/en/

 

Splitting the line would represent a current division, which would not preserve your readings, however you can boost the voltage of your power supply and connect the two devices in series (see Figure 6) to ensure that the loop is still receiving the power it needs. 

Jorr-El
Systems Engineer
Testeract: Automated Test Specialists
0 Kudos
Message 2 of 2
(2,837 Views)