08-04-2014 10:44 PM
I'm trying to control a 3rd party servo drive via EtherCAT:
Using the LabVIEW test panel (see image below), I'm able to toggle the slave between Bootstrap, Init, and Pre Operational states. The LCD on the slave displays the correct states that I selected, so I know that the basic EtherCAT link is working.
However, when I try to transition from Pre Operational to Safe Operational state, I get an error.
I'm at a loss at how to start troubleshooting.
The Error Explanation says "Go to your device's Online Device State page and check the device's error and emergency data". However, I don't see any error or emergency data in the Online Slave Device State page. There's only "EtherCAT: Online: State" and "EtherCAT: Parameters" (image above).
I'm wondering if this issue is related to any of the following:
Any tips would be greatly appreciated!
Solved! Go to Solution.
08-05-2014 11:30 AM
Hey,
It sounds like this issue is very likely caused by not being able to properly import the XML files. I would also double check that you had the correct files from Beckhoff.
Here is an article that might help you as well.
Configuring an EtherCAT Master to Interface with a Beckhoff EtherCAT Coupler
http://digital.ni.com/public.nsf/allkb/99F7EBA04B08A2CA86257A78000CEA36
08-05-2014 09:46 PM
Hi Britton,
Thanks for your response.
The import failure turned out to be a red herring. Thanks to Matthew's help, I was finally able to import the XML file into my cRIO (see the other thread), but this issue persists.
I've carefully looked through the XML files. I imported Beckhoff AX5xxx.xml (attached, with extension changed because the forum rejects *.xml files). It's from the Beckhoff website and it indeed contains an entry for my servo drive, "AX5203-0000 EtherCAT Drive (SoE, 2 Ch.)"
I have already followed every step in your linked article before posting this thread, except for one variation: I added the slave device by using "Existing target or device" -> "Discover an existing target(s) or device(s)". This should be an even more robust process than the manual method shown in that article. See my Project Explorer screenshot above for verification.
Any other ideas? Should I be worried about my empty object dictionary?
08-06-2014 11:51 AM
Hey,
Do you have any signs that you are communicating with the slave successfully? Are you able to transition to any other states?
08-06-2014 06:41 PM
Hey,
Yes, as I wrote in my original post: "Using the LabVIEW test panel (see image below), I'm able to toggle the slave between Bootstrap, Init, and Pre Operational states. The LCD on the slave displays the correct states that I selected, so I know that the basic EtherCAT link is working."
What do you make of the error message? It says "Go to your device's Online Device State page and check the device's error and emergency data", but I can't find any error or emergency data on that page.
08-07-2014 11:52 AM
Hey,
That error message is a general one that's not that helpful. The better one is the one the device itself is giving saying there a problem with the SoE communication layer.
It looks like your connection to your slave is fine, and that the error is specific to the Servo drive profile over Ethercat. I would try to make a simple application in LabVIEW to control the Beckhoff AX5203 to see if you get errors when LabVIEW is automatically handling state transitions.
You may also want to look through the troubleshooting tips listed in this article just to make sure we're not missing something small.
Working with EtherCAT Drives (NI SoftMotion Module)
http://zone.ni.com/reference/en-XX/help/371093M-01/mclvhowto/motionprojectresourcesecatdrive/
08-13-2014 10:47 PM
Thanks again for your suggestions, Britton.
I've been unable to find any LabVIEW VIs that let me control EtherCAT slave states programmatically. Perhaps I'm looking in the wrong place. Could you please show me where to find them?
In any case, I believe that these state transitions are handled at the low-level firmware level, not the high-level (LabVIEW) application level. Here's why I think so:
From these observations, I deduce that the CompactRIO automatically tries to perform the state transitions at startup before loading any software.
Furthermore, I believe that the slave must first be in Operational mode before I can send commands to it, because:
it looks like SoftMotion axes can only be bound to the AKD drives supplied by NI (http://sine.ni.com/nips/cds/view/p/lang/en/nid/209126 ). It doesn't work with my Beckhoff one.
Notice how my drive doesn't show up in the SoftMotion config box:
Before I try anything else, I'd like to find out: Does NI Industrial Communications for EtherCAT support SoE?
08-14-2014 05:51 PM
Hey,
Evidently, NI was unable to obtain the ability to work with Beckhoff, and so only officially supports AKD. Regarding whether NI Industrial Communications for EtherCAT supports SoE, see the response to your other forum post.
08-14-2014 08:54 PM - edited 08-14-2014 08:54 PM
I see. That's a shame, but aattt least now I know why these challenges exist.
Thanks for alll your prompt responses, Britton!
