Folks,
I have a cRIO 9073 with an NI 9474 plugged into slot 6 (other stuff too). I created a project in LV2012 that uses the scan interface. All the devices were recognized and the I/O Variables were created for each I/O point. My VB6 app binds a pushbutton to one of the 9474 channels via the Wizard created I/O variable Mod6 DO0 (Network Published). When I toggle the push button, the output does not change. If I create a Shared Variable and bind it to the I/O variable and in turn bind the pushbutton to the newly created Shared Varible, it works! Why does one method work and the other does not? I don't have an issue when binding an LED to the I/O Varible. I really don't want to duplicate every I/O Varible with Shared Varibles. Any insight would be helpful and appreciated.
Blaine
10-02-2013 06:20 PM
Blaine,
Can you tell us what operating system you're using and give us some more information about your application, and the steps you went through to create these variables? Attaching a screenshot of you code may be helpful in troubleshooting this problem as well.
10-03-2013 02:22 PM
Bryan,
Thanks for jumping on this. I must apologize - what I did in the VB application was set the Access mode of the button connected to the shared variable to Write AutoUpdate. The button connected to the I/O variable had the Access mode set to Write. When I set the mode to Write AutoUpdate, the problem was resolved. Sorry to bother you, Bryan.
Blaine
10-04-2013 02:37 PM
Blaine,
It's no problem at all, I'm glad you were able to get up and running!
Thanks,