WOW!!.. I get to answer my own question. You all are slow... J/K...
Anyway, the fine people at NI Tech Support Helped me out with this one. Seems that it is a problem related to Lookout and Modbus. After discussing this problem with a few engineers, I decided to call the customer and let him know of his mistake. Well, he proceeded to tell me that "Wonderware can do it with out a problem". So I called NI Support again, and they told me that further research showed that it is something that was not put into Lookout. The Support engineer started a "CARD?". But he also gave me a work around.
1. create an expression
2, enter getbit(3,1)
This expression will return a ON status since the number 3 in binary is 1 1 and looking at the first bit is 1.
So for my
application I would use
getbit(modbus1.307682,1)
I hope this makes sense.