OPC data quality bad

I recently added a new rtu to my opc server, it worked fine for a while and then it stopped with ‘bad quality’ for each value in the quick client under the rtu data points. It shows good quality for all items under the ‘rtu_system’ .

 

It started working again after a few days and stopped when I power cycled the RTU.

I can ping it with no packet loss

 

I have two rtu’s on the opc server, the other one is working fine, and I can find no configuration differences between the two.

 

Lookout 6.6

OPC server  4.500.462.0 -u

Windows 7

0 Kudos
Message 1 of 2
(5,433 Views)

I deleted the OPC device in the server and rebuilt it, same problem.

 

I found if I go into properties and disable data collection, wait about 5 minutes then re-enable it, it will come back with good data, I have to wait a period of time before I re-enable it, otherwise it will be bad. Once it is working it continues to work until a prolonged interruption in communications.

 

If I disconnect the Ethernet cable and wait a few minutes, then reconnect it, it will come back with bad data, if I reconnect it within 60 seconds, it will come back with good data.

 

It is definitely a timing issue, but where?