01-08-2017 01:24 PM
We have just upgraded a water treatment plant PLC (GE 90-30 to GE RX3I) but I can't seem to get Lookout 6.7.1 to connect to our W7 server using either the GE SNP 9030 serial driver or the GE Versamax Ethernet driver. I've confirmed solid communication using both serial and ethernet from the GE Machine Edition software without any issues.
Thanks, Win B.
01-09-2017 03:25 AM
Hi,
Did you succeed using Ethernet protocol to connect GE 90-30 to Lookout? I suggest you using OPC server(which is intallered together with Lookout) to have a try, this software also concludes drivers for GE 90-30 to GE RX3I, you can use it to verify if the problem comes from the hardware.
01-09-2017 09:52 AM
Thanks for great info. As soon as we work through the current storms here in NorCal I'll try both of your suggestions.
wb
03-14-2017 11:50 AM
I hope that you have got your solution. Cheers!!!
03-14-2017 12:54 PM
NI OPC Server 2015 did the trick. Thanks.
wb