You have to delete whatever is connected to the modbus Poll Rate datamember (just leave it blank). Connect FALSE (or a Pushbutton) to Poll datamember.
This will avoid the modbus object to poll, or it will just poll when you push the Pushbutton.
However, when you create a new connection to any modbus datamember (e.g. creating an expression to 40001) it will immediately verify the connection and raise the error 'no communication response from modbus secondary'.
To disable this Immediate Poll, the lookout developers implemented once a hidden modbus.ini setting:
[all]
SkipImmediatePoll=1
[mymodbusobject1]
SkipImmediatePoll=0
This setting in your modbus.ini will disable to make the connection verified. (However, not for your mymodbusobject1)
Hope thi
s helps
Roland